can emt be used on the exterior to house romex that is suitable for direct burial?
And any wire installed in any raceway in a wet location, has to be listed for wet location And to go one farther: Until just recently UL pulled the "wet location' listing for all the EMT connectors. There are some that are now listed but that has only been in the last few month's.358.10(B) Corrosion Protection. Ferrous or nonferrous EMT, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth , or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition .
to mean UF.romex that is suitable for direct burial