K KGCastro New member Jun 15, 2011 #1 Is it acceptable for EMT to be embedded in concrete inside building? Article 358.10 does not clearly states Yes or No. Please help because the design of our conduit systems using EMT are embedded, which is not a best practise I believe.
Is it acceptable for EMT to be embedded in concrete inside building? Article 358.10 does not clearly states Yes or No. Please help because the design of our conduit systems using EMT are embedded, which is not a best practise I believe.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 15, 2011 #2 It is permitted. Depending on the application RMC might be a better choice.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 15, 2011 #3 This might be interesting to you: http://forums.mikeholt.com/showthread.php/137352-Conduit-in-concrete?highlight=concrete