Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
Do they make them or just FMC or LFMC? I know they make them for RMC but never seen them specifically for EMT.Thank you.
Thanks. What do you mean “set” the fitting to the middle! Middle of what?You use them for both. Just set the fitting accordingly at install. When it's 50° I set it to middle since that's middle temp for expansion here.
Thank you I appreciate that.You slide a stick of conduit in and screw that side down. The other side slides in and isn't screwed down. You have your expansion amount figured. The one I posted allows 2 inches of expansion or contraction. You either leave 1 inch out or 2 inches out or 0.25" out from all the way tight depending on your install temperature and are good to go.
No problem. Some oddball stuff like this you should get your hands on and just look to see how they work. Do you have a refurbisher or some place that resells used stock that you can go in and just put your hands on the wierd stuff they have. If you get to know the owner they might have all sorts of stories too that may help you out in what your working with in the future.Thank you I appreciate that.
The middle of range of motion and overlap.Thanks. What do you mean “set” the fitting to the middle! Middle of what?
This should be printed on every expansion coupling. Its not but people forget this. Theoretically there shouldn't be much change in length of wire from thermal expansion and contractions but it happens and the wires get pulled by 90s and conduit bodies along with it.The middle of range of motion and overlap.
If it's hot out during installation, you cut the conduits so there is maximum overlap, so they can move apart as they cool. If it's cold, you install with minimal overlap, so they have room to move towards each other.
Don't forget to leave some slack in the wires.
Yes, my companies warehouse or a supply house we have good relationship.No problem. Some oddball stuff like this you should get your hands on and just look to see how they work. Do you have a refurbisher or some place that resells used stock that you can go in and just put your hands on the wierd stuff they have. If you get to know the owner they might have all sorts of stories too that may help you out in what your working with in the future.
Hmmmmm, I'm thinking that when these are installed the overall length of the EMT run never changes. Say if you had a straight run of 500 feet, and you anchored each end solidly. The overall linear distance from end to end would never change, and you'd bever get a sag or a belly. or any kind of deflexionThis should be printed on every expansion coupling. Its not but people forget this. Theoretically there shouldn't be much change in length of wire from thermal expansion and contractions but it happens and the wires get pulled by 90s and conduit bodies along with
I don't have any argument about that. I hate it when someone installs wire too tight in in any applicationAnd to repeat: an expansion fitting needs sufficient slack in the wires so that fitting motion doesn't stress the wires.
I once built a portable guyed antenna tower for ham radio out of pvc conduit. So I set it up nice and straight. The next day I looked and it was crooked, I adjusted the ropes to straighten it. Later that day it was leaning kinda the other way. Long story short, it was leaning opposite from the sun.PVC has a temperature coefficient 5-10x larger than other common building materials.
And that one is only the 3/4" size; I can't imagine a 2" one.wow, talk about sticker shock!!