I am reviewing a job by another engineering firm, They have a 1200A service. They have (4) sets of 4#350KCMIL, in a 2 1/2" C. The wire type called for is thwn-2 or xhhw-2 in their specifications. They have sched 40 pvc, emt, imc, and rigid listed in their specifications.
From my calculations, the only way it fits in a 2 1/2"C is if the conduit is EMT.
I have two questions regarding EMT for this installation:
1.The commentary from the 1999 NEC for 348-4(b) states that generally galvanized steel EMT installed in contact with soil requires supplementary corrosion protection. Is this accurate in your experience?
2. 348-5 (1) states that EMT is not allowed where electrical metallic tubing will be subject to severe physical damage. This installation is going from a CT cabinet to a pad mounted transformer. So there will be a couple feet exposed from the CT cabinet to the where it enters the ground. A riding lawnmower could be driving by this area. Is this considered "subject to severe physical damage"?
From my calculations, the only way it fits in a 2 1/2"C is if the conduit is EMT.
I have two questions regarding EMT for this installation:
1.The commentary from the 1999 NEC for 348-4(b) states that generally galvanized steel EMT installed in contact with soil requires supplementary corrosion protection. Is this accurate in your experience?
2. 348-5 (1) states that EMT is not allowed where electrical metallic tubing will be subject to severe physical damage. This installation is going from a CT cabinet to a pad mounted transformer. So there will be a couple feet exposed from the CT cabinet to the where it enters the ground. A riding lawnmower could be driving by this area. Is this considered "subject to severe physical damage"?