trojans4
Member
- Location
- Iowa
- Occupation
- Semi -retired master electrician. Fully retired math and physics teacher.
I do only residential and only wire with romex. A friend of mine is in the process of building a new house. His father, who was an industrial electrician, wired the house for him. He did the whole house in EMT. Looks very good and neat compared to running romex by the way. My question is this: do you have to run a separate ground wire as an EGC in the EMT? I know that the NEC says in 250.118 that EMT can be used as an EGC. Supposedly the inspector told him he had to run a ground wire in the EMT so he did. I know some localities require residential to be wired in conduit but not in the location or state we live in so I have no experience with this. So, does the NEC require a separate ground wire in EMT? If it does can someone give me a code reference because I couldn't find one.