davet said:If running conduits with parallel conductors in each conduit, (2-2.5" emt"s /
3-350kcm in each pipe / no nuet.) are grounding bushings necessay at both ends?
Dave T
Email address removed.
Use PMs to exchange emails.
iwire
dcspector said:Bond bushings 250.92.... at both ends would be to reduce a Choke Coil effect?
iwire said:Trevor all I would add is that Don has pointed out that the larger concentric KOs found in disconnects etc. are not listed for grounding.
So above 250 volts to ground you may need to use a bonding bushing.
But I agree in general I will not need them in feeders.
flanative78 said:Could you please elaborate on why you would not need bonding bushings on a feeder......