Have conduit that's in a concrete encased ductbank(indoors) and doesn't specify RGS or EMT. Spec says threadless fitting are not permitted to be embedded in concrete. So I guess you have t use RGS. Agree?
 

Ingenieur

Senior Member
Location
Earth
Weird spec
doesn't pvc fare better in concrete?
it's the most common method from what I've seen

spec says must be threaded
I guess a compression fitting has threads although the conduit is not threaded
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Have conduit that's in a concrete encased ductbank(indoors) and doesn't specify RGS or EMT. Spec says threadless fitting are not permitted to be embedded in concrete. So I guess you have t use RGS. Agree?

Along with other things, Schedule 80 PVC can be threaded. But I would generally assume RMC for bidding purposes unless I could get an answer. OR if I felt there might be review and price adjustment later, I would bid it with Schedule 80 and note it prominently in my proposal. It isn't worth losing money if you are forced to use RMC, but it might be the few dollars that gets you a second look.
 

Carultch

Senior Member
Location
Massachusetts
Along with other things, Schedule 80 PVC can be threaded. But I would generally assume RMC for bidding purposes unless I could get an answer. OR if I felt there might be review and price adjustment later, I would bid it with Schedule 80 and note it prominently in my proposal. It isn't worth losing money if you are forced to use RMC, but it might be the few dollars that gets you a second look.

Do there exist PVC couplings with female threads on both ends, that are listed for electrical applications?
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
There is no appearance of any variation of the word "thread" in Article 352.

I apologize for being lazy. Many times I log things in my brain for future use and threading schedule 80 was something I have read about doing at some point. So I got lazy and referenced it. Further search looks like you can thread it because there is no direct prohibition, but why would you when you can just glue a fitting on it.
 