is there any code reference to vertical installations of EMT conduit.
the 358.30 is focused on horizantal applications.

i have been running into this when we are installing a machine where there is no supporting structure in sight. this is due to the manufacturing facility lay out. the unsppoted disyance coulde range between 15ft-20ft

Thank you all for your help
 

mo2004

Member
cord drop is not an option according to the code.

see code 400.7

flexible cord can not be hard wired into junction box. (see 400.7 a3,6,8)

the machines is either will need an outlet or they need to be hard piped.
 

eprice

Senior Member
Location
Utah
Why do you say 358.30 is focused on horizontal appliactions? 358.30(B) applies to horizontal runs, but I see nothing that limits the rest of 358.30 to horizontal runs.

Have you considered using IMC or RMC in the problem locations? Take a look at 342.30(B)(3) and 344.30(B)(3).
 

mo2004

Member
342.30 IMC
344.30 RNC

They have similar requirements for support as EMT. I am not debating weather it needs protection or not. It is just difficult to do so when there is no supporting structure to use for supporting the conduit.

Thank you
 

iwire

Moderator
Staff member
Location
Massachusetts
mo2004 said:
342.30 IMC
344.30 RNC

They have similar requirements for support as EMT.

Yes and no.

Take a moment and look specifically at 342.30(B)(3) or 344.30(B)(3).

Your allowed 20' vertical unsupported for your type of installation.
 