EMT mixed with PVC

Status
Not open for further replies.

satox

Member
My NEC 2008 is not clear on this subject so I am putting this out to you electro-wizards here:

1. Can you connect emt to a PVC (weather proof) outdoor junction box?
2. Are strain reliefs required in the junction box (where the splices will be)?.

I could not find any PVC junction boxes that had strain reliefs . I eventually found a metal box but I'm still curious if there was a problem mixing metal with PVC. This junction box is replaces a rotting wood box that housed an ancient panel.
 

Strife

Senior Member
Really lost on the strain relief.
I guess you can connect the EMT to a pvc box with a female, but even with that I'm at a loss. Why not use a bell box? The problem with EMT to PVC, is the EMT effectively grounded?

My NEC 2008 is not clear on this subject so I am putting this out to you electro-wizards here:

1. Can you connect emt to a PVC (weather proof) outdoor junction box?
2. Are strain reliefs required in the junction box (where the splices will be)?.

I could not find any PVC junction boxes that had strain reliefs . I eventually found a metal box but I'm still curious if there was a problem mixing metal with PVC. This junction box is replaces a rotting wood box that housed an ancient panel.
 

tkb

Senior Member
Location
MA
You can connect EMT to a PVC box using a regular EMT connector or a raintite one if outside.
The only thing is that you will have to use a bonding bushing to connect to the EG.
 

maghazadeh

Senior Member
Location
Campbell CA
There used to be a restriction on this subject in NEC. No metalic conduit Shall enter into a non-metalic box smaller than 100 sq. inches.
I am not aware if that rule has been changed or not. next poster may educate me too.
 

tkb

Senior Member
Location
MA
The blue text is comentary from the 2011 NECH.

314.3 Nonmetallic Boxes

Nonmetallic boxes shall be permitted only with open wiring on insulators, concealed knob-and-tube wiring, cabled wiring methods with entirely nonmetallic sheaths, flexible cords, and nonmetallic raceways.

Exception No. 1: Where internal bonding means are provided between all entries, nonmetallic boxes shall be permitted to be used with metal raceways or metal-armored cables.

Exception No. 1 applies to nonmetallic boxes without threaded entries and permits the use of metal raceways and metal-armored cables with nonmetallic boxes. Internal bonding means must be installed to ensure ground continuity between the metal raceways or metal-armored cables. For the purposes of Exception No. 1, the term metal- armored cable includes cables with a metal covering such as mineral-insulated, metal-sheathed cable (Type MI), metal- clad cable (Type MC), and armored cable (Type AC).

Exception No. 2: Where integral bonding means with a provision for attaching an equipment bonding jumper inside the box are provided between all threaded entries in nonme- tallic boxes listed for the purpose, nonmetallic boxes shall be permitted to be used with metal raceways or metal- armored cables.

Exception No. 2 permits the use of metal raceways and metal-armored cables with listed nonmetallic boxes equipped with threaded entries. An integral bonding means is required to ensure ground continuity between the threaded entries. The requirement for means to attach a bonding jumper accommodates devices or equipment attached to the box. For the purposes of Exception No. 2, the term metal- armored cable includes cables with a metal covering such as mineral-insulated, metal-sheathed cable (Type MI), metal-clad cable (Type MC), and armored cable (Type AC).
 
Last edited: