Can you use EMT outdoors if using rain tight compression connectors or better to go with rigied aluminum ?
What would rain tight fittings be intended for if not for outside installations?Can you use EMT outdoors if using rain tight compression connectors or better to go with rigied aluminum ?
It was more of a q on the emtWhat would rain tight fittings be intended for if not for outside installations?
I am , and that's why I'm asking I see guys using EMT outdoors so I was confusedIf you're in NYC EMT is not permitted in wet locations.
ARTICLE 358
Electrical Metallic Tubing: Type EMT
SECTION 358.10
Subsection 358.10(C) – Delete the subsection in its entirety.
SECTION 358.12
Subsection 358.12(7) – Add a new subsection 358.12(7) to read as follows:
(7) For underground or exterior installations or in wet locations.
I can't help but wonder how often in your career you overlooked a NYC rule It seems to be a different world.Right in the NYC code amendments under uses not permitted:
Yes it is very different starting with the fact that NYC is still under the 2008 NEC and they have about 70 pages of some crazy amendments.I can't help but wonder how often in your career you overlooked a NYC rule It seems to be a different world.
The OP is in New York City.2023 NEC - 358.10(2) Uses Permitted
In dry, damp, and wet locations
Yes it is very different starting with the fact that NYC is still under the 2008 NEC and they have about 70 pages of some crazy amendments.