The DCA inspector made a comment today that the electrical conduits passing through the building’s expansion joint require expansion couplings.
Is this required for EMT passing through the expansion joint? Per my understanding, EMT doesn’t require expansion couplings. The NEC doesn’t implicitly indicate the use of couplings as it does in other conduit type sections e.g. PVC has a sub-section titled 352.44 Expansion Fittings. Also, the coefficient of expansion for EMT conduit is not significant in areas where we don’t have sun exposure like the roof.
I'm considering telling the contractor to install a foot of flex conduit to transition across any joint.
Is this required for EMT passing through the expansion joint? Per my understanding, EMT doesn’t require expansion couplings. The NEC doesn’t implicitly indicate the use of couplings as it does in other conduit type sections e.g. PVC has a sub-section titled 352.44 Expansion Fittings. Also, the coefficient of expansion for EMT conduit is not significant in areas where we don’t have sun exposure like the roof.
I'm considering telling the contractor to install a foot of flex conduit to transition across any joint.