EMT rain tight fittings

Status
Not open for further replies.

crtemp

Senior Member
Location
Wa state
I want to install 3/4'' EMT but it will be outside. I want to do a LB to come out from the existing panel and go about 40 feet to a new sub panel but that side will need a LB also. I'm having trouble finding LB fittings that are listed rain tight. Is there something else I should be using in place of a LB? I usually just use pvc but it will be in a hot area and don't want it warping.
 
To be completely compliant, use an [aluminum] RMC/IMC LB with a close nipple and a Bridgeport 291-RT or its equivalent.

On the other side, if going directly into a KO, use a close nipple with seal ring or sealing locknut on outside and standard rigid locknut on the inside.
 
Rigid and a Myers hub into the box. There currently aren't any UL listed rain tight fittings for emt.

Jason
 
I want to install 3/4'' EMT but it will be outside. I want to do a LB to come out from the existing panel and go about 40 feet to a new sub panel but that side will need a LB also. I'm having trouble finding LB fittings that are listed rain tight. Is there something else I should be using in place of a LB? I usually just use pvc but it will be in a hot area and don't want it warping.

You'll be fine using an aluminum LB and screwing raintighht connectors into each end.
 
Really, that's new to me. Last I knew there weren't any "rain tight" listed connectors that were approved by UL.

"manufacturers of UL Listed “raintight”
compression type EMT fittings
were required to comply with the
more stringent follow-up test re-
quirements. If the manufacturers
of these fittings did not comply
with the new requirements, they
were no longer authorized to mark
their UL Listed fittings with the
“Raintight” marking. Currently, no manufacturer is
authorized to mark their Listed
compression type EMT fittings
with the “Raintight” marking."

That was taken directly from UL's website.

Jason
 
It's possible, I don't do anything outside that allows me to use emt. So I may be completely out of the loop. That's cool if someone actually got approved by UL. That would make a lot of work less expensive than running rigid.

Jason
 
That note about non UL listed raintight fittings is many years old. There are ample manufactures of raintight fittings available, what we use are steel compression and the gland nuts are a different color for raintight. We have boxes of them on our shelf, compression and connectors
 
I want to install 3/4'' EMT but it will be outside. I want to do a LB to come out from the existing panel and go about 40 feet to a new sub panel but that side will need a LB also. I'm having trouble finding LB fittings that are listed rain tight. Is there something else I should be using in place of a LB? I usually just use pvc but it will be in a hot area and don't want it warping.

One more quick question on using the EMT as the EGC. Do I just use a regular lock nut in the original panel or do I need to ground the EMT conduit with a bonding bushing of some kind? There will be a 90 amp OCPD so I wasn't sure if I need to ground the pipe with a #8. Again, sorry for dumb questions but I rarely ever use EMT.
 
One more quick question on using the EMT as the EGC. Do I just use a regular lock nut in the original panel or do I need to ground the EMT conduit with a bonding bushing of some kind? There will be a 90 amp OCPD so I wasn't sure if I need to ground the pipe with a #8. Again, sorry for dumb questions but I rarely ever use EMT.

No special requirements. I'd probably install an equipment ground but, that's just me.
 
You'll be fine using an aluminum LB and screwing raintighht connectors into each end.

I agree, that's how I would do it.

There are almost no connectors listed for use with a threaded hub. They are not investigated for adequate grounding continuity. Connectors have straight threads. Threaded hubs have tapered threads and are intended for threaded RMC or IMC. There are combination conduit bodies listed for RMC, IMC, and EMT... but you will find they are only listed as raintight when used with rigid conduit.
 
It's possible, I don't do anything outside that allows me to use emt. So I may be completely out of the loop. That's cool if someone actually got approved by UL. That would make a lot of work less expensive than running rigid.

Jason
It's not only possible it's true and has been for probably 15 years now. I think every EMT fitting manufacture has a listed raintight line.

Roger
 
One more quick question on using the EMT as the EGC. Do I just use a regular lock nut in the original panel or do I need to ground the EMT conduit with a bonding bushing of some kind? There will be a 90 amp OCPD so I wasn't sure if I need to ground the pipe with a #8. Again, sorry for dumb questions but I rarely ever use EMT.

Note Washington state requires a wire type EGC in EMT outside (WAC 296-46B-358).
 