MM, welcome to the forum! :)

They also make threadless couplings and connectors made specifically for rigid, in both setscrew and compression styles. I believe there are even threadless couplings for joining rigid to EMT.
 

Chev

Master Electrician @ Retired
Location
Mid-Michigan
Occupation
Retired Master Electrician, Formerly at Twin Lakes Electric and GMC
If I'm going from rigid to EMT (and vice versa) I use a set screw connector and screw a threaded coupling on to it.
 

shockin

Senior Member
Around here the wholesale houses don't stock the "dual" listed fittings. They only stock EMT fittings which will work, but they are not listed. I always have them order the correct ones in for me.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
You could also use conduit end adapters

apltonc00003_tw2_2_tr_001.jpg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In the larger sizes they are often listed for both but not the smaller sizes.


As Bob mentioned this is typically in sizes 2.5" and larger. That's because at 2.5" and above EMT and RMC have roughly the same outside diameter.
 