EMT Schedule Size

Status
Not open for further replies.

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
This might be a stupid question but what schedule is EMT? PVC has schedule 40 and 80 but there is no schedule for EMT in the code book. I need to know the schedule because I am specifying a firestopping detail and the firestopping detail says I need schedule 10 or higher pipe.
 
EMT has been adequate in every fire penetration detail I have seen.
Which fire penetration detail do you recommend? I really need this. I think I need a T rating of 1 due to NYC building code. I'm penetrating concrete
 
Each fire stop mfg has systems that are listed for various wall assemblies. I like Hilti, 3M. Hilti has a very good tech support line
 