330.30 Securing and Supporting.
...
(B) Securing. Unless otherwise provided, cables shall be secured
at intervals not exceeding 1.8 m (6 ft). Cables containing
four or fewer conductors sized no larger than 10 AWG
shall be secured within 300 mm (12 in.) of every box, cabinet,
fitting, or other cable termination. In vertical installations,
listed cables with ungrounded conductors 250 kcmil and
larger shall be permitted to be secured at intervals not exceeding
3 m (10 ft).
...
330.40 Boxes and Fittings. Fittings used for connecting
Type MC cable to boxes, cabinets, or other equipment shall
be listed and identified for such use.
The fitting on the cable entry end must be a listed and identified MC cable termination type. 330.30 lists fitting without elaboration, but should be interpreted with the following part, "or other cable termination", to mean a cable termination fitting. AFAIK, this is the only type of fitting that can be associated directly with MC cable :happyyes:. 330.40 confirms the interpretation.Sleeve your MC in EMT & use approiate fittings & I see no problems
You can go as far as you want provided there is a listed MC fitting terminating the MC, as a cable (the cable terminates wherever the sheath is stripped from the conductors), and secured within 12" of the fitting on the cable side. There is no Code which requires the conductors be terminated at any distance beyond the fitting....
Smart $ referenced 330.40 and I agree, then he also said something about EMT only being less than 12"...huh?
I think you can go as far as you want with the EMT, or wiremold etc... I think this is what iwire meant.
By special permission, the authority having jurisdiction
may waive specific requirements in this Code or permit
alternative methods where it is assured that equivalent objectives
can be achieved by establishing and maintaining
effective safety.
Got it. Agreed.You can go as far as you want provided there is a listed MC fitting terminating the MC, as a cable (the cable terminates wherever the sheath is stripped from the conductors), and secured within 12" of the fitting on the cable side. There is no Code which requires the conductors be terminated at any distance beyond the fitting.
I had never considered this, probably won't ever do it. Interesting thought though.If you transition to EMT without a listed MC fitting, you must secure the cable within 12" of the cabinet, box, [less listed MC fitting], or other cable termination... thus limiting the EMT to a maximum of 12", unless you somehow manage to secure the MC cable within the EMT at 12" or less from its entry into the cabinet, box, or other cable termination. There is no Code section which actually requires an MC connector. The closest I can think of at present are 312.5 and 314.17... and 312.5(C) actually states cables must be secured to the cabinet. But neither outright state a cable connector must be used.
Are you transitioning from MC to EMT with a connector?
Or are you just pushing the MC through the EMT with out any type of connector?
If the later how do you bond the MC jacket and how do you protect the wires from the cable jacket?
Yes.
Heck no. :happyno:
I get upset enough when I see guys use electrical tape to hold the anti-short in place insulating the armor from the connector.
We do it a number of ways.
A changeover fitting, sometimes listed for the purpose but sometimes not.
A box or wireway with no splices in it.
And yes, even making changeover fittings with a conduit coupling.
Could be
I would have no issue with sliding unstripped MC through a short section of EMT as a sleave without any connecters at either end.