emt spaced off exterior of commercial building?

Merry Christmas

croyfish

Member
Location
lake station, IN
Occupation
electrician apprentice
had a buddy call me saying his boss chewed him out because he installed EMT on an exterior wall of a commercial building and secured the EMT with 1 hole straps. his boss said it was against code because moisture would build up between the wall and the EMT and cause issues. I've looked through article 110, 300, and 358 and found nothing stating such a thing. has anyone around the Chicagoland area heard of such a thing and if so can you provide the code reference or atleast the location of this information.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
You can’t find the rule as it does not exist. Respectfully ask your boss for a reference.
Welcome to the forum. You will do well with your questioning mind. There are a lot of dinosaurs in our trade.
Note there may be a local code rule on spacing EMT
 
had a buddy call me saying his boss chewed him out because he installed EMT on an exterior wall of a commercial building and secured the EMT with 1 hole straps. his boss said it was against code because moisture would build up between the wall and the EMT and cause issues. I've looked through article 110, 300, and 358 and found nothing stating such a thing. has anyone around the Chicagoland area heard of such a thing and if so can you provide the code reference or atleast the location of this information.
I hope not or else ive got A LOT of EMT to go back and fix after 25+ years 😳
 

BarryO

Senior Member
Location
Bend, OR
Occupation
Electrical engineer (retired)
Note there may be a local code rule on spacing EMT
Always need to keep in mind that the NEC itself is just a publication by the NFPA and has no legal significance until it is referenced in whole or part by local regulation. Always check what is the legally binding regulation is in your area.
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
There's a best practice to do electrical installations. Certainly it would be better to use a 2 piece backstrap or Minerallac strap. This would keep moisture from accumulating at the back of the conduit where it touches the wall thus keeping the conduit from rusting as quickly. These practices are more expensive and more labor intensive so you would need to charge more. There are some instances where the Code specifies that you leave an air space where walls may be washed frequently such as dairies. But for general installations, I concur with the rest of the group. There is nothing wrong with using 1 hole straps.
 

croyfish

Member
Location
lake station, IN
Occupation
electrician apprentice
You can’t find the rule as it does not exist. Respectfully ask your boss for a reference.
Welcome to the forum. You will do well with your questioning mind. There are a lot of dinosaurs in our trade.
Note there may be a local code rule on spacing EMT
thanks. I'm sure some people find me annoying cause I ask questions and "challenge" them on what they say is code but I like to know what I'm doing when I'm doing something. I always ask for references to go read them to further my knowledge. my buddies boss couldn't cite a reference. Just his own preference. thanks for the welcome.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
thanks. I'm sure some people find me annoying cause I ask questions and "challenge" them on what they say is code but I like to know what I'm doing when I'm doing something. I always ask for references to go read them to further my knowledge. my buddies boss couldn't cite a reference. Just his own preference. thanks for the welcome.
In my long career I've heard a thousand things that were "code". Most of the time the person insisting it was "in the book" could not provide a code reference.
 
There is a requirement for article 312 stuff to be mounted with 1/4" gap (312.2), so maybe that is how it started. That happens a lot where someone hears "a cabinet needs a gap if outside" and then someone starts thinking/saying that EVERYTHING needs that gap.
 

JoeNorm

Senior Member
Location
WA
On longer horizontal runs I try to space it off the wall for this reason. Not a code thing but I think it is a best practice. Vertical runs I am not so concerned.
 