steve : ) local613 said:
when roughing in walls that consist of metal studs, do the studs qualify as support for the conduit when the emt is installed through them?:-?

Welcome to the Forum.

358.30 Securing and Supporting.

(B) Supports. Horizontal runs of EMT supported by openings through framing members at intervals not greater than 3 m (10 ft) and securely fastened within 900 mm (3 ft) of termination points shall be permitted.
 