EMT Supported Box or Enclosure

RaffJimT

Member
Location
NH
Occupation
Electrician
Article 314.23 Support of Boxes: I understand from the provisions in this Article of the NEC that Raceway-Supported Boxes can only be supported utilizing Threaded conduit.
EMT (although does not explicitly mention) is not allowed to support a box such as a 4" square metal box using compression type or set screw type connectors. Looking for comment.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
EMT (although does not explicitly mention) is not allowed to support a box such as a 4" square metal box using compression type or set screw type connectors. Looking for comment.
Correct. The box with EMT would require it's own support.

Welcome to the forum.
 

jap

Senior Member
Occupation
Electrician
Correct. The box with EMT would require it's own support.

Welcome to the forum.

Isn't there an exception for EMT to support conduit bodies though ?

Say, a run of emt into a SS or Compression connector threaded into the long or short end of an LB followed by a 4sq box chase nippled into the other end ?

Jap>
 

RaffJimT

Member
Location
NH
Occupation
Electrician
Isn't there an exception for EMT to support conduit bodies though ?

Say, a run of emt into a SS or Compression connector threaded into the long or short end of an LB followed by a 4sq box chase nippled into the other end ?

Jap>
No, The code is definitive on Threaded Raceway - Threaded hub
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
There is an exception for conduit bodies in 314.23(E)

(always pays to check the book :) )
 
  • Like
Reactions: jap

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Wouldn't the EMT into the conduit body still need a support within 3' or is this covered by the exception?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Wouldn't the EMT into the conduit body still need a support within 3' or is this covered by the exception?
The way I read it, yes, but the wording might be subject to interpretation as that is mentioned in the body of the paragraph and not the exception
 

jap

Senior Member
Occupation
Electrician
No, The code is definitive on Threaded Raceway - Threaded hub

Just saying the use of the exception and a conduit body may offer a way to support a box from EMT that's not a hard "no".

You'd still have to follow the rule for support of the conduit body itself.