can EMT be installed under a slab on grade below the gravel and vapor barrier?
From the UL Guide for ferrous rigid conduit (DYIX).In general, galvanized steel electrical metallic tubing in contact with soil requires supplementary corrosion protection. Where galvanized steel electrical metallic tubing without supplementary corrosion protection extends directly from concrete encasement to soil burial, severe corrosive effects are likely to occur on the metal in contact with the soil.
Galvanized rigid steel conduit installed in contact with soil does not generally require supplementary corrosion protection.
"The UL WhiteBook, Category FJMX, states that in general, galvanized steel EMT in contact with soil requires supplementary corrosion protection. Where galvanized steel EMT without supplementary corrosion protection extends directly from concrete encasement to soil burial, severe corrosive effects are likely to occur on the metal in contact with the soil."
Don typed faster than I did!:grin: I need to put down the sandwich...![]()
Ground level no. High rise, 2nd floor and above, yes.
Rain tight connectors and couplings.