I'm having a disagreement with the inspector from a small town here. He is the "Building Official" and does all the inspections for all the trades. He has no one above him that I can appeal to.
The situation is this:
We did a kitchen remodel in a condo on the 5th floor af a 6 story building built in 1975. The service and meters are on the ground floor with a main disconnect for the meter banks (40 units). The meter banks have 125 amp main breakers for each unit right below the meters. Typical meter bank installation. From the meter banks each unit has 1.25 inch emt with 2 # 2 THW and 1 #4 THW CU to the panel in the unit. Meg bushing on both ends of the EMT and bond bars in the unit panels. #6 copper fromthe meg bushing to the bond bar. Neutrals are "floated" in the panels.
The inspector is saying I have to pull an equipment grounding conductor from the meter center to the panel in the unit because I have a 4 wire range receptacle and because I'm installing arc fault breakers on the 3 lighting and receptacle circuits in the panel. He's citing 250.24 (5) as his reason. I'm having a hard time convincing him that the applicable section for this is 250.118 (4) and that he is confusing grounding and bonding.
Any suggestions on how to convince him. Or do you think he is right?
Either way I don't see how we can remove the existing conductors after 39 years and I know we won't be able to add another wire in this pipe without pulling everything out and running the 4 wires back in together.
The situation is this:
We did a kitchen remodel in a condo on the 5th floor af a 6 story building built in 1975. The service and meters are on the ground floor with a main disconnect for the meter banks (40 units). The meter banks have 125 amp main breakers for each unit right below the meters. Typical meter bank installation. From the meter banks each unit has 1.25 inch emt with 2 # 2 THW and 1 #4 THW CU to the panel in the unit. Meg bushing on both ends of the EMT and bond bars in the unit panels. #6 copper fromthe meg bushing to the bond bar. Neutrals are "floated" in the panels.
The inspector is saying I have to pull an equipment grounding conductor from the meter center to the panel in the unit because I have a 4 wire range receptacle and because I'm installing arc fault breakers on the 3 lighting and receptacle circuits in the panel. He's citing 250.24 (5) as his reason. I'm having a hard time convincing him that the applicable section for this is 250.118 (4) and that he is confusing grounding and bonding.
Any suggestions on how to convince him. Or do you think he is right?
Either way I don't see how we can remove the existing conductors after 39 years and I know we won't be able to add another wire in this pipe without pulling everything out and running the 4 wires back in together.