EMT

Status
Not open for further replies.

grosonke

Member
Is Emt allowed to be used outside if so I havent seen any connectors or coupling that look raintight enven though listed. I also recieved a statement from Mike holt about Emt fittings removing the claim of being raintight any one know about this? I think 2002 code states you can?
 

slicer

Member
Re: EMT

225.10 provides the approval for using EMT in outside installations on the surface of buildings as long as the circuit is not over 600 volts.
All fittings must be "listed" for use in wet locations.
 