Table 300.50 identified minimum duct cover requirements for both general and special conditions. These minimum cover depths would seem appropriate for direct buried ducts but do not seem to recognize the benefits or protection of concrete encasement. For example a rigid steel conduit need only have 6 inches of cover whereas a nonmetallic conduit requires 18 inches of cover. If the nonmetallic conduit were encased and 3 inches beneath the top of the encased bank, would that not provide equivalent protection to the RGS conduit and allow a shallower depth.
Similarly, could not a concrete-encased duct bank be less than 24 inches beneath a parking lot surface?
If you have technical references permitting shallower depths for concrete-encased ducts, I'd appreciate those references.
Similarly, could not a concrete-encased duct bank be less than 24 inches beneath a parking lot surface?
If you have technical references permitting shallower depths for concrete-encased ducts, I'd appreciate those references.