I have a 230 VAC 0.07 Amp enclosure exhaust fan, and need advice on protection device selection and calculation. Any advantage of fuse vs breaker?
IMO a 15 amp breaker is just as effective for short circuit protection. As mentioned such fans are almost always impedance protected. This protects your wiring from overcurrent. Most any fuse or breaker you use that is 15 amps or less protects your wiring from short circuits. If the motor has failed it needs replaced anyway - what is the point of selecting a device to protect the motor in this case?Thanks for the guidance, I thought there was an actual code based calculation for this, but wasn't sure if applying Table 430.52 would be right for this device. Found a 0.5A 2 pole mini breaker that should work for short circuit protection.
Ok, but if the fan has failed, it still cost $51.00 to replace it whether it trips a breaker or not20A branch circuit supplying panel. Fan $51.00, breaker ebay surplus $8.60.