ayates

Member
I design controls for custom equipment where typically 480vac is brought into the enclosure and then stepped down from there to power items in the enclosure. We feed the 480vac through a panel mounted disconnect with the disconnect handle located on the outside of the enclosure. If the disconnect is "on" the disconnect handle has to be defeated in order to open the enclosure. The job I am working on now we are bringing in 120vac into the enclosure. Does the disconnect have to be done the same way at this voltage level?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I design controls for custom equipment where typically 480vac is brought into the enclosure and then stepped down from there to power items in the enclosure. We feed the 480vac through a panel mounted disconnect with the disconnect handle located on the outside of the enclosure. If the disconnect is "on" the disconnect handle has to be defeated in order to open the enclosure. The job I am working on now we are bringing in 120vac into the enclosure. Does the disconnect have to be done the same way at this voltage level?
Are you bringing in 120V in addition to or instead of the 480V?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I know of no general requirement (except in NFPA 79) that any enclosure must have an integral externally operated disconnect to remove all power.
 

pfalcon

Senior Member
Location
Indiana
I design controls for custom equipment where typically 480vac is brought into the enclosure and then stepped down from there to power items in the enclosure. We feed the 480vac through a panel mounted disconnect with the disconnect handle located on the outside of the enclosure. If the disconnect is "on" the disconnect handle has to be defeated in order to open the enclosure. The job I am working on now we are bringing in 120vac into the enclosure. Does the disconnect have to be done the same way at this voltage level?

This is usually a requirement in keeping with NFPA79 for industrial machinery.

See NFPA79:2007 6.2.3 Enclosure Interlocking

Voltage levels are at or above 50vac (rms) or 60vdc.
 