lu302dan said:I have an enclosure with a ground bar installed in it with the grounds from 120 volt 20 amp circuits landing on this ground bar rather than landing at the loadcenters. What size ground wire do I need to tie this enclosure ground bar to the loascenter's ground bar?
crossman said:Really, you only need one EGC from the panel to the ground bar, and it only needs to be sized for the largest circuit in the enclosure.