Energi Savr Node

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
So I think I can run the 0-10v wiring in the same raceway as the 120v as long as both insulations are rated for 600v. Correct?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So I think I can run the 0-10v wiring in the same raceway as the 120v as long as both insulations are rated for 600v. Correct?

The 0-10 volt wiring would have to reclassified as Class1. In some cases Lutron allows the Class2 control to be reclassified as Class1 so the 0-10 volt conductors can be in the same raceway or cable. You would need to clarify this for the ESN.
 
Status
Not open for further replies.
Top