noonan Member Location Bucks County, PA Occupation Electrical Project Manager Mar 25, 2008 #1 We have a corporate requirement that a manhole needs to be de-energized before entry. Granted, this is the safest way, but is it a code requirement?
We have a corporate requirement that a manhole needs to be de-energized before entry. Granted, this is the safest way, but is it a code requirement?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Mar 25, 2008 #2 Code? Not necessarily. But see 100 Qualifed Person, 110.16 and 110.26 Whats the voltage? Is it a confined space? Your employer should be commended.
Code? Not necessarily. But see 100 Qualifed Person, 110.16 and 110.26 Whats the voltage? Is it a confined space? Your employer should be commended.
noonan Member Location Bucks County, PA Occupation Electrical Project Manager Mar 25, 2008 #4 tom baker said: Code? Not necessarily. But see 100 Qualifed Person, 110.16 and 110.26 Whats the voltage? Is it a confined space? Your employer should be commended. Click to expand... 13.8kV. Yes, it is a permit-required confined space. As for our employer we usually, condemn them.
tom baker said: Code? Not necessarily. But see 100 Qualifed Person, 110.16 and 110.26 Whats the voltage? Is it a confined space? Your employer should be commended. Click to expand... 13.8kV. Yes, it is a permit-required confined space. As for our employer we usually, condemn them.