Energized panels

Status
Not open for further replies.

tyreeinc

Member
Location
Virginia
In a IBX it is required to remove the dead front from the panel in order to IR the panel. The problem I have is all the engineers keep accidentally knocking breakers off by hitting them with the dead front. Does anyone know of any item available to protect the breakers from being turned off because if they are turned off we loose customer servers. Most of the breakers are single pole 20 amp cutler hammer 120V.
 

mxslick

Senior Member
Location
SE Idaho
Yep, there is an easy way..install breaker locks on all the breakers before removing the dead front..remember that breaker locks can be used to lock breakers ON as well as off. (Fire alarm breakers are usually locked on to prevent accidental turn-off.)

Breaker locks for single-pole breakers are cheap and can be ordered in quantity.
 

tyreeinc

Member
Location
Virginia
I have thought about breaker locks but I would have to have 42 per panel and the way we sometimes have to turn them on and off it doesn't seem practicle. Also some are so close to full load if you start touching them they have the tendency to turn off. I was looking for something more in line with protecting them all.
 

480sparky

Senior Member
Location
Iowegia
I have thought about breaker locks but I would have to have 42 per panel and the way we sometimes have to turn them on and off it doesn't seem practicle. Also some are so close to full load if you start touching them they have the tendency to turn off. I was looking for something more in line with protecting them all.


Do like this:

loto4.jpg


DSC_2423a.jpg


loto5.jpg
 

tyreeinc

Member
Location
Virginia
Thanks 480 Sparky

Thanks 480 Sparky

The ones on the single pole breakers that you have in the picture is something like I am looking for do you know who the manufacture is?
 