I am looking if anyone has a solution to my problem.
We have an energized equipment with roughly 2,000V DC that has water cooling loops attached to it. This is construction equipment out in the field. The water loop is a DI system that is closed loop.
The problem we had was one of the hoses had metal brading as the manufacture shipped the wrong ones. This energized the pump panel that smoked a hose.
I am looking for a device that can detect a voltage potential gerater than 50V to 2000V DC between the equipment and ground. If it could have a switch/relay that i could have tied into the power source that would also be helpful.
My main problem right now is finding something that is rated for 2000V DC.
I am looking at a ground fault detector and putting a CT on the positive and negative leads. Then tripping the main if too much stray current is detected. But we are dealing with large amounts of current so i think maybe a voltage detection would be less nussance tripping and more practical. So just to detect a voltage differential between any equipment and the ground.
I have grounded all the equipment here maybe putting CTs on the ground cables and looking for currents on that? I am going with a Star grounding pattern where each pice of equipment is grounded and brought back to the source, so putting a CT on that main ground?
I am worried about nussance tripping and want something that will be reliable in the field. So i feel voltage detection would be the ideal way to go.
Thoughts?
We have an energized equipment with roughly 2,000V DC that has water cooling loops attached to it. This is construction equipment out in the field. The water loop is a DI system that is closed loop.
The problem we had was one of the hoses had metal brading as the manufacture shipped the wrong ones. This energized the pump panel that smoked a hose.
I am looking for a device that can detect a voltage potential gerater than 50V to 2000V DC between the equipment and ground. If it could have a switch/relay that i could have tied into the power source that would also be helpful.
My main problem right now is finding something that is rated for 2000V DC.
I am looking at a ground fault detector and putting a CT on the positive and negative leads. Then tripping the main if too much stray current is detected. But we are dealing with large amounts of current so i think maybe a voltage detection would be less nussance tripping and more practical. So just to detect a voltage differential between any equipment and the ground.
I have grounded all the equipment here maybe putting CTs on the ground cables and looking for currents on that? I am going with a Star grounding pattern where each pice of equipment is grounded and brought back to the source, so putting a CT on that main ground?
I am worried about nussance tripping and want something that will be reliable in the field. So i feel voltage detection would be the ideal way to go.
Thoughts?