091008-1026 EST
The Iceman:
Describe the devices you are seeing. You indicate power factor optimization. This implies a capacitor because of the likelihood of a residential application. Note: synchronous motors can be used for power factor correction, but these would only appear in an industrial application.
If various people can provide sufficient evidence of clear fraud, then it should be possible to get attorney generals of states to start looking into this problem.
We should be looking for any proof that could be used to prove that customers have been duped.
1. What claims were made verbally or in writing by the seller relating to how the devices work, would save energy and/or money, and payback time.
2. What demonstrations were given to prove to the customer that the device reduces energy consumption.
The typical demonstration I have seen is a small single phase motor with no mechanical load, a current meter (not a power meter), and a switch to insert and remove the the power factor correction device. With the power factor correction device as part of the load the input current drops substantially as is expected. Note: a normal induction motor is at its worst power factor point with no mechanical load.
What really happens when the power factor correction capacitor is added to the circuit is no change whatever from the motor terminals to the motor load, in other words no change in the power input to the motor, but the capacitor itself actually adds power loss to the combination due to the small losses within the capacitor. It may require high quality instruments to prove this point.
An area that needs consideration is whether there are errors in the normal KWH meters such that adding the power factor correction causes a lower reading. If this occurs, then with a moderately good KWH meter the error should be small, and therefore not worth very much.
I will conjecture that in many homes that a 25% reduction in energy consumption can be achieve without the purchase of any energy conservation equipment simply by turning off loads when they are not needed.
Results of an Experiment:
Motor:
Import drill press with spindle load, but not drilling, 1/2 HP ToYang.
Capacitor:
Sprague AB 1201 21-25 mfd 125 V at least 30 years on shelf. This is an electrolytic capacitor and has higher losses than a good PF correction capacitor. However, the fraud people seem to be selling relatively good quality capacitors.
Power Meter:
Kill-A-Volt
Capacitor alone --- 20 W 153 VA 1.21 A
Motor alone ------- 355 W 690 VA 5.62 A
Cap and motor ---- 374 W 589 VA 4.81 A
Note the capacitor losses added to the motor power consumption. No energy saving.
scottam99:
What was this $4100 device(s)?
.