I have a 10 story building I am about to bid on (energy managment), and wanted to run some numbers by you guys and maybe you could tell me what you think
The building has 11 AHU's, and each AHU has a HWV, a CHWV, a DAT, Stop Start, Status, Outside Air damper, Freezestat, Smoke Detector, Mixed Air Temp
118 VAV's
16 Exhaust Fans
4 RTU's
1 Remote Chiller Yard
1 Split Unit (DX)
1 Boiler
1 HWP
1 CHWP
I'm thinking in the neighborhood of $47,000, but was curious about what some of ya'll think. The building is going to be retrofit, so the only conduit that needs to be installed is at each AHU (approx. 80' per unit). Thanks!
The building has 11 AHU's, and each AHU has a HWV, a CHWV, a DAT, Stop Start, Status, Outside Air damper, Freezestat, Smoke Detector, Mixed Air Temp
118 VAV's
16 Exhaust Fans
4 RTU's
1 Remote Chiller Yard
1 Split Unit (DX)
1 Boiler
1 HWP
1 CHWP
I'm thinking in the neighborhood of $47,000, but was curious about what some of ya'll think. The building is going to be retrofit, so the only conduit that needs to be installed is at each AHU (approx. 80' per unit). Thanks!