I was amazed today to learn that the ubiquitous 48 inch T12 energy saving lamp has a minimum start temperature of 60?F and must be sheltered from drafts even at that temperature.
Is this a further nail in the coffin of an "old" technology?Watt-Miser ? , Watt-Miser ? Plus, F28T8/UMX and Energy Efficient (/EE) lamps are intended for use where ambient temperatures are 60 F (16 C) or higher and where the lamp surface is protected from strong air drafts. Failure to protect the lamp surface may result in reduced life, poor starting or erratic operation, such as flickering or spiraling. All T12 Watt-Miser ? lamps are intended for use on two-lamp, indoor, lead, high power factor ballasts and are not recommended for use with dimming or reduced current systems. The use of T12 Watt-Miser ? lamps on single lamp ballasts may shorten lamp life. T12 Rapid Start Watt-Miser ? lamps are intended for use only with Rapid Start Ballasts. F40 Rapid Start Watt-Miser ? lamps on high frequency electronic systems may display erratic starting before end of life. T8 Watt-Miser ? lamps are intended for use only with instant start ballasts. F28T8/UMX lamps are designed for use on UltraMax ballasts.