hi,
this may be a dumb question but i figured i would ask it..
if i run a device at 120 vac and it draws 10 amps...
would the same device draw 5 amps @ 240
or does it just split between legs at 240?
thanks
gw
This is a very good point that I not too long ago realized in a thread here. I can't remember what thread it was, but LarryFine and I exchanged posts and he made me realize what you just said, which in all of my years in the trade I never knew it or ran across it. But now I know, and knowing is half the battle.Not always in the case of a resistive heater. If you took a 120 volt that pulled 10 amps and put 240 to it then it would draw 20 amps. It would however give the same heat at 5 amps 240 volt that it would 120v 10 amps. You did say "energy use" so then yes 120v at 10 amps is the same energy as 240 at 5
---- if i run a device at 120 vac and it draws 10 amps...
would the same device draw 5 amps @ 240 ----
Conversely, if you took a 240V 4800W construction heater (ignoring the fan motor at the moment)...Not always in the case of a resistive heater. If you took a 120 volt that pulled 10 amps and put 240 to it then it would draw 20 amps. It would however give the same heat at 5 amps 240 volt that it would 120v 10 amps. You did say "energy use" so then yes 120v at 10 amps is the same energy as 240 at 5
Not always in the case of a resistive heater. If you took a 120 volt that pulled 10 amps and put 240 to it then it would draw 20 amps. It would however give the same heat at 5 amps 240 volt that it would 120v 10 amps. You did say "energy use" so then yes 120v at 10 amps is the same energy as 240 at 5
Conversely, if you took a 240V 4800W construction heater (ignoring the fan motor at the moment)...
4800W / 240V = 20A
240V / 20A = 12 ohms
...and connected it to 120V:
120V / 12 ohms = 10A
120V x 10A = 1200W
You wind up with a functioning heater that consumes 1/4 the power. (without the messy fire that would follow usage of a 120V heater at 240V) Of course this neglects the fan motor, so don't try this at home...
hOw do you know that your world you live in is real and not a bizarro world?Mike, I live in a real world, I do not connect 120 equipment to 240, but thanks for adding confusion to the thread.![]()
hOw do you know that your world you live in is real and not a bizarro world?![]()
Mike, I live in a real world, I do not connect 120 equipment to 240, but thanks for adding confusion to the thread.![]()
There are "constant power" devices, motors generally being in this category. Double the voltage, and you will reduce the current by half, and the power will remain the same (not a surprise, since we are talking about constant power devices).
There are "constant impedance" devices, resistance heaters and incandescent lights being in this category. Double the voltage, and you will double the current, and the power drawn will go up by a factor of four.
Double the voltage on any device that is not rated for the higher voltage, and you may very well destroy it.
There are no dumb questions, except perhaps the ones not asked.
I don't know how energy meters work. But the two configurations you described will, in fact, consume the same amount of energy during any given hour. That is because your two loads are the same amount of watts, with a watt being the rate of using energy.Will the energymeter in a 3 phase supply . . . read same units consumed in one hour. . . .