Have you ever known something was a code requirement and then proceeded to do research biased on what you thought was right? Only to be wrong?
I am starting to detail a new job. It?s a central plant and information technology building for a new hospital. In the central plant there is an ?enginator.? A natural gas powered generator designed to run one chiller when electricity prices get to high. It is connected to two chillers via a series of transfer switches. Under normal conditions the two chillers run on utility power. If electricity rates climb the enginator starts and can run either chiller, not both.
Anyway the grounding system was all over the place on the drawings so I was putting together what was required. The enginator did not have a grounding electrode system. Even though it has a different name it is still just a generator (480/277Y) and is going to need to be grounded right? I look at the transfer switches and they are all 3 pole so my first thought is we are going to have to make sure the neutral point of the enginator is not bonded to the frame so we don?t create a down stream neutral to bond connection. All the feeds have only the phase conductors and an equipment grounding conductor so I am thinking all these feeds need a grounded conductor sized per 250.66 for a fault return path.
Then a light turns on in my head (thanks to someone else). We do not have any line to neutral loads so we are not pulling a neutral (obviously). By definition the enginator is now a separately derived system even with the 3 pole ATS? because there is no grounded conductor tying the service grounded conductor to the enginator neutral point. The enginator can have a neutral to ground bond and everything is just fine!
Am I missing something? Or have I got my head clear now.
PS: I realize since we are not serving line to neutral loads the system is not required to be grounded. I believe it was intended to be it was just missed.
Nick
I am starting to detail a new job. It?s a central plant and information technology building for a new hospital. In the central plant there is an ?enginator.? A natural gas powered generator designed to run one chiller when electricity prices get to high. It is connected to two chillers via a series of transfer switches. Under normal conditions the two chillers run on utility power. If electricity rates climb the enginator starts and can run either chiller, not both.
Anyway the grounding system was all over the place on the drawings so I was putting together what was required. The enginator did not have a grounding electrode system. Even though it has a different name it is still just a generator (480/277Y) and is going to need to be grounded right? I look at the transfer switches and they are all 3 pole so my first thought is we are going to have to make sure the neutral point of the enginator is not bonded to the frame so we don?t create a down stream neutral to bond connection. All the feeds have only the phase conductors and an equipment grounding conductor so I am thinking all these feeds need a grounded conductor sized per 250.66 for a fault return path.
Then a light turns on in my head (thanks to someone else). We do not have any line to neutral loads so we are not pulling a neutral (obviously). By definition the enginator is now a separately derived system even with the 3 pole ATS? because there is no grounded conductor tying the service grounded conductor to the enginator neutral point. The enginator can have a neutral to ground bond and everything is just fine!
Am I missing something? Or have I got my head clear now.
PS: I realize since we are not serving line to neutral loads the system is not required to be grounded. I believe it was intended to be it was just missed.
Nick