MikeyL
Member
- Location
- South Carolina
I hope I'm not starting off on the wrong foot. I'm here to learn & willing to share what little knowledge I do have.
Unfortunately my question doesn't stem from an area that I have much experience with.
Anyways, here is my question:
I'm in the process of erecting a 24' x 56' x 14' steel building (steel frame- primered, nothing isolating column to beam to siding). I'm forming a monolithic slab with rebar at it's lowest point 2' below the six main and two roll up door columns with 6" wire mesh in between. 200A seperate service will be brought in.
I spoke with the inspector and asked what he needed to see in regards to grounding the building itself. He stated that nothing was required but it was "a good idea".
What I'm asking for is the wise thing to do and/ or some references to point me in the right direction & to aid in my understanding.
Thanks!
Unfortunately my question doesn't stem from an area that I have much experience with.
Anyways, here is my question:
I'm in the process of erecting a 24' x 56' x 14' steel building (steel frame- primered, nothing isolating column to beam to siding). I'm forming a monolithic slab with rebar at it's lowest point 2' below the six main and two roll up door columns with 6" wire mesh in between. 200A seperate service will be brought in.