JFletcher
Senior Member
- Location
- Williamsburg, VA
We are doing a commercial project for an ice skating rink. The service to it is supplied by a 45kVA 480/208Y xfmr. However, due to future use/expansion, we are setting a 600A fused disco, and the prints call for 2 runs of 4 wires 500MCM (8 500s plus ground, which I *think* is 3 or 4/0) thru one 4" PVC conduit. My question is wouldnt it have been cheaper to run 2+ conduits and much smaller copper rather than jam it all in one pipe and eat the derating? If I am calculating correctly, 4 runs of 4 4/0 or 250 MCM thru 4 smaller pipes would suffice. Or one set of 1000MCM thru one pipe (specs call for copper so AL is out). I assume the engineer isnt a moron, so what am I missing?
Also, the project calls for 3 ground rods vs 2. Why? What is that extra rod gonna do? Not that I mind that, more materials, more labor, more money, just wondering if there is some benefit of which I am unaware for a third ground rod.
Also, the project calls for 3 ground rods vs 2. Why? What is that extra rod gonna do? Not that I mind that, more materials, more labor, more money, just wondering if there is some benefit of which I am unaware for a third ground rod.