Engineering supervision…
Isaiah
Baton Rouge
Electrical Inspector
In general can “engineering supervision” overrule the NEC?
Examples: 240.86(A), 310.10(G)(1) exception.
No, engineering supervision is a provision of the NEC, not a way to overrule it.
I have worked many factory / Industrial calls in my career.
Many if not most think that with the job under the auspices of an engineer, they go against the NEC.
A few of those times pointing out NEC violation got me laid off!!
That didn't happen on the Minooka co-gen
When I entered the industry some 50 years ago many heavy industrial facilities, particularly in the 'rust belt" region, were not subject to state AHJ control and inspections after the original building construction. However, over the past few decades, insurance costs and litigation have caused many of these states to apply the NEC to all installations, however many processes and machines are still not routinely inspected.
Had an engineer tell me once " I have no problem with it so we're going to do it"
He backed off after it was pointed out:
1. You can't override the code
2. The company will not allow this since we know it's a code violation and can't be defended in court.
An engineer can only invoke "engineering supervision" in situations where the NEC explicitly allows it.
He didn't care. He saw no problem with it.
Code or no code.
He came around to our way of thinking once he realized we weren't going to allow him to bluff his way through.
I don't think "supersede" is the correct word. I would say "engineering supervision" is an alternate method that is allowed sometimes.
Yes. If it is a provision of the NEC it does not supersede the NEC. 705.12(B)(6) does not supersede the other provisions of 705.12(B).
I agree completely so far.
Well, yes it does, because it effectively says so, explicitly. But only those specific sections it mentions, and that's all internal to 705.12(B), not to mention the internal to the NEC.
Speaking as an engineer, I would not want the power to overrule the NEC, nor would I want the risk (financial and professional) that it would entail. Furthermore, there are things the NEC allows an engineer to do that I would never choose to do. You want examples? Perhaps after I have another cup of coffee. 😉