This is in regards to 2023 NEC. My question is does 220.5 rounding to the nearest whole number apply to microinverter output conductor sizing and OCPD of backfed breaker?
With 17 enphase IQ8M-72-2-US microinverters, each having max continuous output current of 1.35A, per 705.28(A), the total power source max current is calculated as:
17 x 1.35A = 22.95A
And per 705.28(B), the conductor ampacity is calculated as:
22.95A x 1.25 = 28.6875A, or 28.69A using appropriate significant digits.
For 18 microinverters, the total max current per 705.28(A) is:
18 x 1.35A = 24.30A
And the conductor ampacity is:
24.30 x 1.25 = 30.375A, or 30.38A
Does 220.5(B) permit the dropping of the 0.38 fraction of an ampere to arrive at 30A? And would this permit a 30A rated disconnect, and a 30A rated OCPD backfed breaker to be used for this?
705.30(B) specifies OCPD sized not less than the maximum currents calculated in 705.28(A). 705.28(A) and 705.28(B) both contain the wording "Where not elsewhere required or permitted in this code". If 220.5(B) which is "permitted elsewhere in the code" for feeder conductors, can be applied after the 705.28(A) calculation that arrives at 24.3A, with the .3 dropped and the value used is 24A, then the conductor ampacity and the OCPD required would be 24 x 1.25 = 30A.
Doing so would permit 30A disconnect, and a 30A backfed breaker, instead of a 60A disconnect and 35A breaker.
This seems logical to me, what do you say?
With 17 enphase IQ8M-72-2-US microinverters, each having max continuous output current of 1.35A, per 705.28(A), the total power source max current is calculated as:
17 x 1.35A = 22.95A
And per 705.28(B), the conductor ampacity is calculated as:
22.95A x 1.25 = 28.6875A, or 28.69A using appropriate significant digits.
For 18 microinverters, the total max current per 705.28(A) is:
18 x 1.35A = 24.30A
And the conductor ampacity is:
24.30 x 1.25 = 30.375A, or 30.38A
Does 220.5(B) permit the dropping of the 0.38 fraction of an ampere to arrive at 30A? And would this permit a 30A rated disconnect, and a 30A rated OCPD backfed breaker to be used for this?
705.30(B) specifies OCPD sized not less than the maximum currents calculated in 705.28(A). 705.28(A) and 705.28(B) both contain the wording "Where not elsewhere required or permitted in this code". If 220.5(B) which is "permitted elsewhere in the code" for feeder conductors, can be applied after the 705.28(A) calculation that arrives at 24.3A, with the .3 dropped and the value used is 24A, then the conductor ampacity and the OCPD required would be 24 x 1.25 = 30A.
Doing so would permit 30A disconnect, and a 30A backfed breaker, instead of a 60A disconnect and 35A breaker.
This seems logical to me, what do you say?