This is large equipment - 110.26(C)(2) because it is for equipment rated 1200 amperes or more and over 6 ft wide that contains overcurrent devices, so there needs to be one entrance to and egress from the required working space not less than 24 in. wide 6-1⁄2 ft high at each end of the working space.
One end of the working space for the 4000A SWBD is mostly against the column and a small portion extends past the column at that end. Of course this is an interpretation for the local AHJ, but I'm curious if anyone would have trouble saying that there is still an one entrance to and egress from that end of working space not less than 24 in. wide 6-1⁄2 ft high, since you can go around the column?

One end of the working space for the 4000A SWBD is mostly against the column and a small portion extends past the column at that end. Of course this is an interpretation for the local AHJ, but I'm curious if anyone would have trouble saying that there is still an one entrance to and egress from that end of working space not less than 24 in. wide 6-1⁄2 ft high, since you can go around the column?