Re: Entrance to Working Space
Doesn't 110.26(C)(2) stop on the outside of the electric room?
In other words inside the electric room you need a clear and unobstructed path to the electric room door but once outside the electric room the 110.26(C)(2) requirements end.
I know many people dislike the handbook but I will go for it anyway.
If you look at Exhibits 110.12, 110.14, 110.15 and 110.16 in the handbook it seems the code is only concerned with the inside of the electric room.
Specifically with one door you should not have to walk around the switch gear that is experiencing a fault to get to the door.
110.26(C)(2) A single entrance to the required working space shall be permitted where either of the conditions in 110.26(C)(2)(a) or (b) is met.
(a)Unobstructed Exit. Where the location permits a continuous and unobstructed way of exit travel, a single entrance to the working space shall be permitted.
(b)Extra Working Space. Where the depth of the working space is twice that required by 110.26(A)(1), a single entrance shall be permitted. It shall be located so that the distance from the equipment to the nearest edge of the entrance is not less than the minimum clear distance specified in Table 110.26(A)(1) for equipment operating at that voltage and in that condition.
I do not see that those sections require a clear path to outside the building just a clear path to outside the electric room.
That said the Code that Dave put up may take over once outside the electric room.