2000 NFPA 101 Life Safety Code
7.1.10.2 Furnishings and Decorations in Means of Egress.
7.1.10.2.1
No furnishings, decorations, or other objects shall obstruct exits, access thereto, egress therefrom, or visibility thereof.
I do not see that those sections require a clear path to outside the building just a clear path to outside the electric room.110.26(C)(2) A single entrance to the required working space shall be permitted where either of the conditions in 110.26(C)(2)(a) or (b) is met.
(a)Unobstructed Exit. Where the location permits a continuous and unobstructed way of exit travel, a single entrance to the working space shall be permitted.
(b)Extra Working Space. Where the depth of the working space is twice that required by 110.26(A)(1), a single entrance shall be permitted. It shall be located so that the distance from the equipment to the nearest edge of the entrance is not less than the minimum clear distance specified in Table 110.26(A)(1) for equipment operating at that voltage and in that condition.
This is slightly off topic, and I can?t back it up with a code reference, but here?s my interpretation. Suppose you go through one door into an electric room. Suppose the other side of the electric room has another door that leads to a storage room from which there is no other exit. I believe that you can only count the electric room as having one door. Since the second door has no path to the outside world, it does not count.Originally posted by iwire: Doesn't 110.26(C)(2) stop on the outside of the electric room? In other words inside the electric room you need a clear and unobstructed path to the electric room door but once outside the electric room the 110.26(C)(2) requirements end.
I?ll go one step further. If, as you stand in front of an electrical panel, the one and only one door to the room is on your right, and if the hinges to the panel?s front cover are on the right side, so that the open panel cover is between you and the exit door, you have a violation. I consider the panel?s front cover as being an ?obstruction,? in the context of 110.26(C)(2).Specifically with one door you should not have to walk around the switch gear that is experiencing a fault to get to the door.