2-223 Log #2962 NEC-P02 Final Action: Accept in Principle
(210.52(A))
_______________________________________________________________
Submitter: Joseph Whitt, JW Electric
Recommendation: New text:
210.52(A) General Provisions. In every kitchen, family room, dining room,
living room, parlor, library, den, sunroom, bedroom, recreation room, foyer, or
similar room or area of dwelling units, receptacle outlets shall be installed in
accordance with the general provisions specified in 210.52(A)(1) through (A)
(3).
Substantiation: Today?s homes are being built with larger foyers some being
as large as other rooms in the dwelling. As the code now stands, this area will
be considered a hall which would require only one receptacle if it is more than
ten feet in one direction no matter the other direction. With the addition of
foyers to 210.52(A) it will reduce the possibilities of a homeowner running
extension cords under rugs and through doorways of the foyer to power table
lamps and other appliances.
Panel Meeting Action: Accept in Principle
The panel does not Accept the insertion of the word ?foyer? as recommended
in the proposal. Instead, the panel has created a new section (I) to read as
follows:
?(I) Foyers. Foyers that have an area that is greater than 60 ft2 shall have a
receptacle(s) located in each wall space as defined in 210.52 (A)(2)(1).?
Panel Statement: The panel has added a new subdivision ?(I) Foyers? for
clarity. The panel has also added a minimum area requirement to this section to
exempt smaller foyers that typically do not have the space to facilitate home
furnishings and electrical equipment.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 10 Negative: 2