OK Sparky 93
- Iridea14Strat
- Electrician
Instead of being in the middle of, which has already happened, I suppose it better to start another similar thread. With a different title.
Am I understanding or not?
Permanent spas or pools.
So 680.26 equipotential bonding
(A) performance. We can agree on
(1) conductive pools
Manufactured tub is not
(2) perimeter surfaces
First sentence says shall include unpaved surfaces and other types of paving.
Last sentence says for no conductive pool shells bonding at four points shall not be required.
At this point, I don’t think anything needs to be done for a manufactured listed hot tub.
(3) metallic components
Don’t think we have that issue
(4) underwater lighting
Most likely not
(5) metal fittings
Maybe if built in to the ground. But we have a manufactured listed unit. Mess with it or modify it and bye bye listing.
(6) electrical equipment - I believe everything is bonded at the factory, which is satisfied via EGC
(7) Fixed metal parts - this might be the real concern and we are allowed a few exceptions.
Most likely not
(5) metal fittings
