EPO Wiring OK to Run with Feeder?

Status
Not open for further replies.

scotteng

Member
Location
Apollo Beach, FL
Occupation
Professional Engineer
We are designing the addition of a generator on a strip retail tenant who is somewhat remote from the metering service equipment. AHJ requires the generator EPO to be at the service equipment. Running a new conduit for EPO control wiring would require routing through a number of existing tenant spaces which the LL desires to avoid. We are pulling a new 3/0 CU tenant feeder in an existing 2"C to increase service to 200A.

Is there anything that would prevent us from running the EPO control wiring with the tenant feeder conductors?

Thanks!
 
We are designing the addition of a generator on a strip retail tenant who is somewhat remote from the metering service equipment. AHJ requires the generator EPO to be at the service equipment. Running a new conduit for EPO control wiring would require routing through a number of existing tenant spaces which the LL desires to avoid. We are pulling a new 3/0 CU tenant feeder in an existing 2"C to increase service to 200A.

Is there anything that would prevent us from running the EPO control wiring with the tenant feeder conductors?

Thanks!

I would think, off the top of my head, that you could do it if you create a class 1 control circuit. Isolate your new class 1 circuit at the at the genset with a relay interfaced to the genset control system. I would use DC for the new control circuit to avoid capacitance issues, especially on a long run like this. I think I would be inclined to run at aleast a #10 to avoid damaging the control wires while pulling with larger other conductors.
 
Last edited:
I would think, off the top of my head, that you could do it if you create a class 1 control circuit. Isolate your new class 1 circuit at the at the genset with a relay interfaced to the genset control system. I would use DC for the new control circuit to avoid capacitance issues, especially on a long run like this. I think I would be inclined to run at aleast a #10 to avoid damaging the control wires while pulling with larger other conductors.

I might add that you could even get creative and use a 3 wire system and have EPO buttons at the service and at the tenat space with a reset button only at the genset.
 