Ok how about this:Act like this is Jepordy and phrase that in the form of a question!
#4 is the correct size grounding electrode conductor for a 200 amp service, which should run to within 5' of the entrance of the metallic water pipe.cold water bond is also a #4 if it is not the grounding electrode why is it not sized to the maximum over current protection
Too bad, you could have used #6.200amp service is grounded by a #4 bare to a 8 foot ground rod.
You mention a 200 amp service, and now you want to size your water bond to a 30 amp branch circuit? This doesn't make any sense. Can you please clarify, and use full sentences?which is 30 amp to the water heater
The bond to the grounding electrodes is not supposed to be part of the fault clearing path, so the size of the CB is not an issue.Originally posted by rearea1:
200amp service is gounded by a #4 bare to a 8 foot ground rod. cold water bond is also a #4 if it is not the grounding electrode why is it not sized to the maximum over current protection which is 30 amp to the water heater
Look at 250.104(A)(1).cold water bond is also a #4 if it is not the grounding electrode why is it not sized to the maximum over current protection which is 30 amp to the water heater