Hi, I have a situation where there is an existing 4" under ground conduit with 3 #6, 1 #10 GND THHN coming from a service entrance, entering a pull box, and then continuing on to a 60A panel. I would like to reuse this conduit, re-pulling the #6's with additional 3 #1 and a #8 ground from a new 100A disconnect to a new 100A panel (continuing on from the pull box in a new 1-1/2" conduit.) Should I remove the existing #10 GND in the 4" conduit (since I will have a new #8 there)? Do I bond the #10 GND that goes to the 60A panel to the new #8 GND inside the pull box? What would you do? I've calculated that the 90 deg THHN meets the adjustment factor for 6 current carrying conductors, but I'm a little stumped on the equipment ground(s).