We have an existing 3 phase 2400V delta secondary ungrounded distribution system that we are converting to high resistance grounded with the addition of a zigzag grounding transformer. The only required wiring interconnect from the transformer to the system disconnect (breaker) consists of the equipment bonding jumper and CT circuit to the relay controlling the breaker. The current design has a copper conductor bonding jumper and CT circuit (single unshielded conductors) routed in one RMC (conduit will be bonded to bonding jumper both ends). My fear is that any ground fault current in the equipment bonding jumper (effectively the conductor and conduit in parallel) could/will induce errors in CT circuit. Shouldn't the CT circuit be routed in its own conduit? Any help appreciated.