greenspark1
Senior Member
- Location
- New England
Hi all. Outdoors in a C1D2 area I have a skid mounted piece of 480V pre-manufactured equipment consisting of two 45 kW resistance heaters, a couple small motors (<5hp), and some ancillary controls. It is fed by a dedicated feeder from a panelboard breaker indoors out of sight. Once at the skid power is split and protection provided for each piece of equipment: each heater with fuses, CBs for the motors, and fuses for the controls. The question is if the whole assembly requires a primary disconnecting means outdoors at the equipment.
I intend to use the breaker as the disconnecting means but am looking for any Code requirements otherwise. There are separate CBs for the motors on the skid. I don't believe the equipment falls under 430 since the motors are relatively minor. 424.19 does not require the disconnecting means to be within sight of the unit. Especially since this is C1D2, I'd like to keep redundant disconnects out of the area.
I intend to use the breaker as the disconnecting means but am looking for any Code requirements otherwise. There are separate CBs for the motors on the skid. I don't believe the equipment falls under 430 since the motors are relatively minor. 424.19 does not require the disconnecting means to be within sight of the unit. Especially since this is C1D2, I'd like to keep redundant disconnects out of the area.