I have a 3D printer that is listed to operate at 200V to 240V with a 36 FLA listing. I don't have the KVA, KW, or HP of the equipment. So my question is the 36A listing for 200V? If so what would be the FLA at 208V and 240V? Thanks
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
It would most likely be at the 240 volt rating, but because it may be some kind of switching power supply it could be across the board.
 
I would think the FLA is the current draw at the most extreme conditions all around. Depending on the type of load and power supply, that could be at the highest acceptable voltage or the lowest. Feed it with a variac and let us know the results ;)
 