Electron_Sam78
Senior Member
- Location
- Palm Bay, FL
I'm going to be rewiring my first corner grounded delta (200a, 3ph, 480V) service and am doing some research into it. I know I need to use straight rated breakers or if slash rated the minimum voltage rating must be that of the corner grounded system. I also know that the grounded leg must be identified by gray or white marking throughout the installation.
I need to set up one service with 2 individual 100a service disconnects. I'd like to use a MLO panel from the meter can with 2 100a circuit breakers installed for the service disconnects. How should I wire the grounded phase in this equipment?
1).Use 3 pole breaker/panelboard and grounded phase from meter can to the neutral bar then from neutral bar to a lug of panelboard?
or
2). Use a 2 pole breaker/panelboard and grounded phase from meter can to neutral bar and then grounded phase from neutral bar out to load?
Also, if I wanted to use fused disconnects instead of breakers, I couldn't use a 3 phase DC with the grounded phase fused since that wouldn't allow for simultaneous opening of all phases should the neutral be lost (I assume that's the reason behind the simultaneous opening). I would have to use a single phase DC with the grounded phase wired through a bus bar, correct?
I need to set up one service with 2 individual 100a service disconnects. I'd like to use a MLO panel from the meter can with 2 100a circuit breakers installed for the service disconnects. How should I wire the grounded phase in this equipment?
1).Use 3 pole breaker/panelboard and grounded phase from meter can to the neutral bar then from neutral bar to a lug of panelboard?
or
2). Use a 2 pole breaker/panelboard and grounded phase from meter can to neutral bar and then grounded phase from neutral bar out to load?
Also, if I wanted to use fused disconnects instead of breakers, I couldn't use a 3 phase DC with the grounded phase fused since that wouldn't allow for simultaneous opening of all phases should the neutral be lost (I assume that's the reason behind the simultaneous opening). I would have to use a single phase DC with the grounded phase wired through a bus bar, correct?